That is a definite gray area, it requires deciding what a structure is and whether you have one. The 2017 definitions:it is in an open field and attached to a 4x4
"Structure. That which is built or constructed, other than equipment."
"Equipment. A general term, including fittings, devices, appliances, luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation."
So is the 4x4 equipment or not? Maybe it's an "apparatus used in connection with an electrical installation." Or maybe not.
If the 4x4 is not equipment, it's a structure, and you need a GES. If it is equipment, it's not a structure (as the panel is certainly equipment), and you don't need a GES.
Further comments:
1) Maybe many GESs are actually a good idea in this context? Although if there is any earth voltage gradient, you'll end up with current flow on all the EGCs.
2) Does the article on RV parks not address this question? I haven't checked.
Cheers, Wayne