JakeS
Member
- Location
- inland empire
- Occupation
- Inspector 1
Maybe some one can shed some light on this for me. In my short period as a residential inspector electric has never really been my strong point. Every CALBO class I have been sent to / senior inspector I have talked to has always brought up the breaker rule, the 120% rule and the center-fed rule being not to exceed 100% of the busbar ampacity. But a electrical engineer pointed out section 705.12 (d) A connection at either end but not both ends, of a center-fed panelboard in dwellings shall be permitted where the sum of 125 percent of the power source(s) output circuit current and the rating of the overcurrent device protecting the busbar does not exceed 120 percent of the current rating of the busbar. Sooo center-fed panels would fall under the 120% rule in the 2019 CEC ?