MNSparky
- Minneapolis, MN
- Electrical Contractor - 2023 NEC
We do a lot of wiring for HVAC contractors as far as reconnects and new installations, we do not preview any of them and the HVAC salesperson is usually worthless in getting us info so we go into nearly all of them blind. I'm trying to think outside the box for a solution to the new 210.8(F) that requires GFCI protection for exterior outlets (other than lighting) which of course includes ACs and ductless units. We run into all different brands of panels so carrying all the different brands and amp ratings in GFCI breakers will be a crazy amount of money to carry on each truck. Not to mention there are those panels that we can't get a gfci breaker for (FPE, Bulldog, fuse, Zinnsco, etc).
The idea I came up with is use a Spa panel in place of the disconnect for the equipment. We could size the breaker in the panel to the required size per the equipment and use the spa panel with built in 50amp GFCI breaker as the GFCI protection. My question is does the GFCI breaker need a neutral run back to the panel to operate correctly? In other words, will it operate correctly if the white pigtail that comes off the breaker is capped as we wouldn't have a neutral at the equipment on reconnect situations?
Or does anyone else have a better idea?