2020 - NEC 230.62 (C)
. . . . So my initial inference is that QO2200RBE does not have any such factory provision. . . .
Anyway, given 230.66, the OP can just read the label of the QO2200RBE and see if it states it is SUSE.
Model number typos, I meant QO2100BNRB which is what the link in post #8 references.
Anyway, if the photo below is current, then the QO catalog is wrong, and the answer in post #16 is correct.
Cheers, Wayne
Possibly this product was originally listed as SUSE under the old standard that didn't require the line side barriers, but that listing is no longer up to date because it hasn't been redesigned or relisted with barriers available?
What's the connection to the water pipe that you mentioned in post #26?
I found my mistake. The metal water pipe inside the basement would be identified as a grounding electrode, which essential needs to be terminated to the grounded conductor via neutral. I terminated the water bond on the grounding bar installed in the disconnect.
Thanks, Rob
Thanks, Rob
Yeah, you mentioned bond but it sounds like the water pipe actually qualifies as a grounding electrode so it's connected by the GEC to neutral.