2020 NEC 705 question

Status
Not open for further replies.
He said it was connected to the service through a disconnect with 700A fuses.

The use of 700A fuses with a 600A panel is a tell that someone just didn't keep track of what they were doing.

Thank you I got that.
I will say from an NEC perspective it's an oops.

I would like to add what if it had a 600 amp main with 700 amp conductors and a proper sized EGC between the service disc and combiner.

I have a few more questions as well. He did ask for others perspective.
 
...

I would like to add what if it had a 600 amp main with 700 amp conductors and a proper sized EGC between the service disc and combiner.
...

The equipment needs to be rated for 125% of the full output of the connected inverters. If that number is 600A or less then there's no need for 700A conductors or fuses, those things could be 600A. If it is more than 600A, then adding a 600A main breaker solves nothing: it might trip.
 
I have a few more questions as well. He did ask for others perspective.
Ask away, but please do not focus on the fuse sizing in the PV AC disconnect; I should have left that detail out because it is a separate issue. My only question is whether 705.12(B)(3) needs to be complied with in an MLO inverter AC combiner panel connected to service conductors through a fused disconnect. I say yes, and so far everyone else has agreed.
 
Ask away, but please do not focus on the fuse sizing in the PV AC disconnect; I should have left that detail out because it is a separate issue. My only question is whether 705.12(B)(3) needs to be complied with in an MLO inverter AC combiner panel connected to service conductors through a fused disconnect. I say yes, and so far everyone else has agreed.
Thank you. Before I comment further I want to get a full picture.
 
Thank you. Before I comment further I want to get a full picture.
What further information do you need? My question is pretty simple; see the bolded text in your post. There's a fused PV AC disconnect between an AC inverter combiner panel and a set of service conductors on the line side of an MDP. Does 705.12(B)(3) apply to the busbars in the combiner panel or not? I am convinced that it does, but I told the electrician (he disagrees) on the project that I would do my due diligence on the question.
 
What further information do you need? My question is pretty simple; see the bolded text in your post. There's a fused PV AC disconnect between an AC inverter combiner panel and a set of service conductors on the line side of an MDP. Does 705.12(B)(3) apply to the busbars in the combiner panel or not? I am convinced that it does, but I told the electrician (he disagrees) on the project that I would do my due diligence on the question.
The intent of the 705.12 rules is meant for mixed use panels, at and after the point of interconnection. The underlying reason for rules such as the 120% rule, and its 100% counterpart for same side feeding, is to avoid the blindspot created when a panelboard filled with a lot more loads than its rating (as is routine) is fed from two sources. An adversarial user could deliberately turn everything on and create an unprotected overload. This situation doesn't happen for a dedicated AC combiner, even if it hosts a few insignificant loads.

Given that the 120% rule allows a 400A panelboard and 80A interconnected source at the opposite end to supply 480A worth of current to the loads, it really isn't any different of a situation for the panelboard's thermal integrity, to have 400A worth of inverter current (after the 125% factor) and loads of negligible current. As long as it is arranged so busbar current is subtractive instead of additive.
 
The intent of the 705.12 rules is meant for mixed use panels, at and after the point of interconnection. The underlying reason for rules such as the 120% rule, and its 100% counterpart for same side feeding, is to avoid the blindspot created when a panelboard filled with a lot more loads than its rating (as is routine) is fed from two sources. An adversarial user could deliberately turn everything on and create an unprotected overload. This situation doesn't happen for a dedicated AC combiner, even if it hosts a few insignificant loads.

Given that the 120% rule allows a 400A panelboard and 80A interconnected source at the opposite end to supply 480A worth of current to the loads, it really isn't any different of a situation for the panelboard's thermal integrity, to have 400A worth of inverter current (after the 125% factor) and loads of negligible current. As long as it is arranged so busbar current is subtractive instead of additive.
The 120% rule and the 100% rule , which are the 2020 NEC articles 705.12(B)(3)(2) and 705.12(B)(3)(1), respectively, both require the OCPD protecting the busbar to be considered in the calculations; this severely limits the size of a PV system that can be connected in a given panel. In 2014 what is in the 2020 NEC as 705.12(B)(3)(3) was brought in specifically to enable the use of AC combiner panels, and it is the only option under 705.12(B)(3) which allows the OCPD protecting the busbar to be omitted from the calculation. It allows for loads to be connected in the same panel as breakers backfed from PV inverters, but it does not require them, i.e. the panel does not have to be mixed use.

But the question is whether 705.12(B)(3)(3) must be complied with for PV inverter combiner panels connected to service conductors. My contention is that the PV AC fused disconnect, by being connected to the service conductors, is governed by 705.11, but the individual inverters in the panel are connected on the load side of that OCPD and therefore are load side connected and governed by 705.12. There are no bus qualifying rules in 705.11 because it only applies to a single inverter connected on the supply side of the MSD. Incidentally, if the breakers in the panel were to fall under 705.11 rather than 705.12, loads would not be allowed in it that are not on the list in 230.82.
 
I have many times voiced my frustration at the language at the beginning of 2020 NEC 705.11. It states, "An electric power production source, where connected on the supply side of the service disconnecting means as permitted in 230.82(6), shall comply with 705.11(A) through (E)." It begs the question as which serivce disconnecting means they are referring to. It should read something like, "An electric power production source, where connected on the supply side of a service disconnecting means as permitted in 230.82(6), shall comply with 705.11(A) through (E). OR "An electric power production source, where connected on the supply side of the service disconnecting means of the premises loads as permitted in 230.82(6), shall comply with 705.11(A) through (E).

By using the word "the" to describe "the service disconnecting means", it kind of implies that there is only one serivce disconnecting means, which would logically be the service disconnecting means serving the premises loads, and not the PV system disconnect. That was how I initially interpreted the language when it first came out. I think the language is sufficiently unclear, which gives ggunn's adversary a leg to stand on in the argument.
 
I have many times voiced my frustration at the language at the beginning of 2020 NEC 705.11. It states, "An electric power production source, where connected on the supply side of the service disconnecting means as permitted in 230.82(6), shall comply with 705.11(A) through (E)." It begs the question as which serivce disconnecting means they are referring to. It should read something like, "An electric power production source, where connected on the supply side of a service disconnecting means as permitted in 230.82(6), shall comply with 705.11(A) through (E). OR "An electric power production source, where connected on the supply side of the service disconnecting means of the premises loads as permitted in 230.82(6), shall comply with 705.11(A) through (E).

By using the word "the" to describe "the service disconnecting means", it kind of implies that there is only one serivce disconnecting means, which would logically be the service disconnecting means serving the premises loads, and not the PV system disconnect. That was how I initially interpreted the language when it first came out. I think the language is sufficiently unclear, which gives ggunn's adversary a leg to stand on in the argument.
It really comes down to me, since I will be asked to affix my PE seal on the design. So far, I am not convinced that the ambiguity in the 2020 NEC supports the electrician's interpretation on this point.
 
So far, I am not convinced that the ambiguity in the 2020 NEC supports the electrician's interpretation on this point.
(More a response to everyone else than to you directly) While the aforementioned ambiguity exists within 705 (as well as some of the definitions in Article 100), the argument from post #14 is unrebutted.

If the PV line side connection is made via a wire splice, then the PV-leg wires coming out of that splice can only comply with 240.21 if they are Service Conductors, which requires that they terminate in a Service Disconnect.

Cheers, Wayne
 
Incidentally, if the breakers in the panel were to fall under 705.11 rather than 705.12, loads would not be allowed in it that are not on the list in 230.82.
That depends on whether the panel is supplied under 230.40 Exception #2 or Exception #5.

But it is worth noting that if the 700A fused disconnect in the OP were eliminated, and if the monitoring breakers were relocated to a subpanel supplied via a feeder tap/splice to one of the inverter output circuits connected to one of the 5 remaining breakers in the 600A panel, then the install would be NEC compliant (for the 2017 NEC and earlier, where service disconnects are not required to be in individual enclosures/compartments). There would be no issue with the fact that 2*200 + 3*80 > 600.

So it is a bit odd that adding a fused disconnect in front of (on the utility side of) the 600A panel renders the installation no longer NEC compliant.

Cheers, Wayne
 
That depends on whether the panel is supplied under 230.40 Exception #2 or Exception #5.

But it is worth noting that if the 700A fused disconnect in the OP were eliminated, and if the monitoring breakers were relocated to a subpanel supplied via a feeder tap/splice to one of the inverter output circuits connected to one of the 5 remaining breakers in the 600A panel, then the install would be NEC compliant (for the 2017 NEC and earlier, where service disconnects are not required to be in individual enclosures/compartments). There would be no issue with the fact that 2*200 + 3*80 > 600.

So it is a bit odd that adding a fused disconnect in front of (on the utility side of) the 600A panel renders the installation no longer NEC compliant.

Cheers, Wayne
It's not relevant because the AHJ in question is enforcing the 2020 NEC, although every AHJ I have dealt with would balk at adding five more service disconnects for a PV system. They typically require a single handle to disconnect all the PV.
 
every AHJ I have dealt with would balk at adding five more service disconnects for a PV system. They typically require a single handle to disconnect all the PV.
FWIW, 2020 NEC 230.71(B) clearly does allow 2-6 PV disconnects: "Two to six service disconnects shall be permitted for each service permitted by
230.2 or for each set of set-vice-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5." 230.40 Exception #5 is the relevant one for PV systems, covered under 230.82(6).

That's also one of the examples of language in 230 that implies a PV disconnect is a service disconnect.

Cheers, Wayne
 
FWIW, 2020 NEC 230.71(B) clearly does allow 2-6 PV disconnects: "Two to six service disconnects shall be permitted for each service permitted by
230.2 or for each set of set-vice-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5." 230.40 Exception #5 is the relevant one for PV systems, covered under 230.82(6).

That's also one of the examples of language in 230 that implies a PV disconnect is a service disconnect.

Cheers, Wayne
Local interconnection guides are not bound by the NEC; they are free to amend them with more stringent requirements and they frequently do. Also, many AHJs require the metering of PV production, and all that I have dealt with require a single PV meter and a single disconnect. The AHJ in question is one of those.
 
Local interconnection guides are not bound by the NEC; they are free to amend them with more stringent requirements and they frequently do.
Ah, I was interpreting AHJ as building department, but you are using it to include the POCO as well. IIRC you deal with some jurisdictions where the POCO is municipal and this distinction is rather blurred?

Certainly POCOs may have requirements on top of the NEC.

Cheers, Wayne
 
Ah, I was interpreting AHJ as building department, but you are using it to include the POCO as well. IIRC you deal with some jurisdictions where the POCO is municipal and this distinction is rather blurred?
Yes, I do, and this is one of those, but to me the AHJ is whatever authority has jurisdiction over the design and installation of a PV system I am working on. Sometimes there are more than one.
 
This is why I wanted to get a full picture of the install to base my decision on.
For what's it's worth, Free.
Basing it on the combiner only will not provide a clear answer.
If the disconnect is considered service disconnect and labeled as such per NEC and a GEC is landed there. Then the install is on the load side of a service disconnect.
There there is no question from there.

Since it is on the load side of a service disconnect the tap location ( line side or load side) is no longer a consideration when reading forward.

In 2020 the word panle board was removed so any buss is now included. This combiner buss now falls under 2020 where in 2017 it would not.

I can now say the install must comply with 705 B (3) and the correct lable installed.
The combiner has load connections so it is fed from two sources.

I don't see how it can be argued any different. The key for me is the label and the confirmation of the disconnect as it's not real clear in 2020. The designer can simple show the GEC at the disconnect and refer to the correct labeling.

Now for the part you did not ask for.
Since the disconnect will be a service disconnect. The conductors between the disconnect and combiner are feeders. Refer to definitions in artical 100, there for rules apply. The combiner (equipment) has a main lug buss. Over current and ground fault and short circuit protection is required to meet the label on the equipment and NEC rules apply protecting the feeder and equipment.

Good read and thanks for sharing.
On a personal note, your the PE that put his stamp on it.
I always say if if don't feel right don't do it.
 

Attachments

  • Screenshot_20231111-111517.png
    Screenshot_20231111-111517.png
    290 KB · Views: 3
Thanks for all your input. I am going to tell them that in order for me to seal a design, under virtually all circumstances under the 2020 NEC, inverter AC combiner panels must comply with 705.12(B)(3), and that most of the time the governing code will be 705.12(B)(3)(3).
 