Sorry to beat a resi dead horse but I’ve recently done a third service change with this “not service equipment” variation and third inspector wanted something slightly different than the other two
First inspector had me unbond my metal water line because it might be plastic underground. I was simply bonding the metal by the service equipment and had two ground rods already. She said she doesn’t let anyone bond the waterline anymore because it’s a false sense of security. I said that if the inside still has metal this bond in theory might provide a better fault path.
Second inspector had me remove bond screw from the “emergency disconnect, not service equipment” effectively leaving that metal case of the disconnect with no fault path (PVC in and out). He tells me I can land the GEC anywhere in or upstream of the service equipment as long as it’s service rated. I took this to mean the GEC can terminate in the Emergency Disconnect, not service equipment - which is service rated but not being used as service equipment in my case. And he agreed (thoughts ?)
Third inspector tells me to put the bond screw in the “emergency disconnect, not service equipment” (I agree) and that the bare copper GEC must be extended with an irreversible splice from the emergency disconnect up 18” into the meter enclosure
Anyone able to clesr
Up with code citations ? I have one I can post relating to the GEC origination location but not sure I’m interpreting correctly
Thanks
First inspector had me unbond my metal water line because it might be plastic underground. I was simply bonding the metal by the service equipment and had two ground rods already. She said she doesn’t let anyone bond the waterline anymore because it’s a false sense of security. I said that if the inside still has metal this bond in theory might provide a better fault path.
Second inspector had me remove bond screw from the “emergency disconnect, not service equipment” effectively leaving that metal case of the disconnect with no fault path (PVC in and out). He tells me I can land the GEC anywhere in or upstream of the service equipment as long as it’s service rated. I took this to mean the GEC can terminate in the Emergency Disconnect, not service equipment - which is service rated but not being used as service equipment in my case. And he agreed (thoughts ?)
Third inspector tells me to put the bond screw in the “emergency disconnect, not service equipment” (I agree) and that the bare copper GEC must be extended with an irreversible splice from the emergency disconnect up 18” into the meter enclosure
Anyone able to clesr
Up with code citations ? I have one I can post relating to the GEC origination location but not sure I’m interpreting correctly
Thanks