The 2023 First Draft Report has been published a few days early. It is found at nfpa.org/70, and select next edition. The public comment closing date is August 19, 2021.
do we have to pay to comment Don?The 2023 First Draft Report has been published a few days early. It is found at nfpa.org/70, and select next edition. The public comment closing date is August 19, 2021.
Above where you see the First Draft Report, there is a line that says " Submit a Public Comment". You click on that to submit a comment. You really have to use both as you can't see the PIs or the text in legislative style in the version of TeraView where you submit the comments.OK, apparently I don't understand the interface--I can see the First Draft Report in Terraview, see my PIs and the responses, but I don't see how to make a Public Comment. The Public Comments are to be linked to a PI, right? So the option to create one should be on the screen that shows the PI?
Cheers, Wayne
do we have to pay to comment Don?
~RJ~
No cost, just register with a name and an email address. If you have registered for the free viewing of the NEC or other NFPA documents, that same registration works for submitting comments.do we have to pay to comment Don?
~RJ~
No, you just have to agree to the website terms of abuse and privacy encroachment policy, which some may consider “paying.”do we have to pay to comment Don?
~RJ~
No.. just to be heard ....do we have to pay to comment Don?
~RJ~
So maybe I'm confused about Public Comments--are they the same format wise as Public Inputs, just relative to the 2023 First Draft rather than relative to the 2020 NEC? Meaning I just go to the First Draft section in question, propose a textual change, and then perhaps in the Public Comment text reference the Public Input involved?You click on that to submit a comment. You really have to use both as you can't see the PIs or the text in legislative style in the version of TeraView where you submit the comments.
Yes, you go to the submit public comment, and put your comment in. You have to go back to the First Revision report and get the PI and/or the FR number associated with your PC.So maybe I'm confused about Public Comments--are they the same format wise as Public Inputs, just relative to the 2023 First Draft rather than relative to the 2020 NEC? Meaning I just go to the First Draft section in question, propose a textual change, and then perhaps in the Public Comment text reference the Public Input involved?
It does not prevent you from submitting a comment that is not related to a FR or a resolved PI, but such comments would be "new material". New material is not permitted to be introduced at the comment stage, so no action will be taken on a PC that introduces new material.This would allow one to make a Public Comment that has no associated Public Input, is there any point in doing that? Are changes ever made based on Public Comments for issues that didn't get a Public Input?
Cheers, Wayne
[PS For 215.2(A)(1)(a) I'm going to propose adding the text "before the application of any adjustment or correction factors in accordance with 310.14." since the CMP seems to be having trouble understanding the error in the current text.]
Is it me or does "210.24 Branch-Circuit Requirements — Summary." Seem wrong, as 240.4(D)(2) will allow 16 Awg copper for the new 10 Amp branch circuits?
installations under exclusive control of electrical utility where such installation … consist of service drops or service laterals, and associated metering, or…
110.12 - Electrical equipment shall be installed in aneatprofessional andworkmanlikeskillful manner.
210.6 Branch Circuit Voltage Limitations- (A) Occupancy Limitation
In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following:
(1) Luminaires
(2) cord-and-plug connected loads 1440 volt-amperes, nominal, or less than 1/4 hp.
I think were entering our second wave of aluminum taking over residential, last one was in the 70's.210.18 adds the 10A circuit. Why? Lighting? Are we going to see 16/2 NM?
I dont see anything prohibiting 16 AWG copper if the conditions of 240.4(D)(2) are met.10 amp circuits are to permit the use of 14 AWG copper clad aluminum. While there are 10 amp breakers and 10 amps has been added to the list of standard OCDP sizes in 240.6, there are no 10 amp AFCI breakers, so will not be able to use 10 amp circuits in most parts of a dwelling unit.
(A) Minimum Size of Conductors.
The minimum size of conductors for voltage ratings up to and including 2000 volts shall be 14
AWG copper or 12 AWG aluminum or copper 16 AWG copper, 14 AWG copper -clad
aluminum, or 12 AWG aluminum , except as permitted elsewhere in this Code.