2023 First Draft Report

Status
Not open for further replies.

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
OK, apparently I don't understand the interface--I can see the First Draft Report in Terraview, see my PIs and the responses, but I don't see how to make a Public Comment. The Public Comments are to be linked to a PI, right? So the option to create one should be on the screen that shows the PI?

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
OK, apparently I don't understand the interface--I can see the First Draft Report in Terraview, see my PIs and the responses, but I don't see how to make a Public Comment. The Public Comments are to be linked to a PI, right? So the option to create one should be on the screen that shows the PI?

Cheers, Wayne
Above where you see the First Draft Report, there is a line that says " Submit a Public Comment". You click on that to submit a comment. You really have to use both as you can't see the PIs or the text in legislative style in the version of TeraView where you submit the comments.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Is it me or does "210.24 Branch-Circuit Requirements — Summary." Seem wrong, as 240.4(D)(2) will allow 16 Awg copper for the new 10 Amp branch circuits?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
You click on that to submit a comment. You really have to use both as you can't see the PIs or the text in legislative style in the version of TeraView where you submit the comments.
So maybe I'm confused about Public Comments--are they the same format wise as Public Inputs, just relative to the 2023 First Draft rather than relative to the 2020 NEC? Meaning I just go to the First Draft section in question, propose a textual change, and then perhaps in the Public Comment text reference the Public Input involved?

This would allow one to make a Public Comment that has no associated Public Input, is there any point in doing that? Are changes ever made based on Public Comments for issues that didn't get a Public Input?

Cheers, Wayne

[PS For 215.2(A)(1)(a) I'm going to propose adding the text "before the application of any adjustment or correction factors in accordance with 310.14." since the CMP seems to be having trouble understanding the error in the current text.]
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
OK, I slogged through submitting my first Public Comment. So I see now that the interface is the same as for Public Inputs, except at the end one must specify a "related item" which is a previous public input or public comment. So that answered my questions above.

Still a poorly designed interface, when viewing a Public Input, one should be able to hit a button to start writing a Public Comment that is linked to the Public Input shown.

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
So maybe I'm confused about Public Comments--are they the same format wise as Public Inputs, just relative to the 2023 First Draft rather than relative to the 2020 NEC? Meaning I just go to the First Draft section in question, propose a textual change, and then perhaps in the Public Comment text reference the Public Input involved?
Yes, you go to the submit public comment, and put your comment in. You have to go back to the First Revision report and get the PI and/or the FR number associated with your PC.
This would allow one to make a Public Comment that has no associated Public Input, is there any point in doing that? Are changes ever made based on Public Comments for issues that didn't get a Public Input?

Cheers, Wayne

[PS For 215.2(A)(1)(a) I'm going to propose adding the text "before the application of any adjustment or correction factors in accordance with 310.14." since the CMP seems to be having trouble understanding the error in the current text.]
It does not prevent you from submitting a comment that is not related to a FR or a resolved PI, but such comments would be "new material". New material is not permitted to be introduced at the comment stage, so no action will be taken on a PC that introduces new material.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Is it me or does "210.24 Branch-Circuit Requirements — Summary." Seem wrong, as 240.4(D)(2) will allow 16 Awg copper for the new 10 Amp branch circuits?

I think 14 AWG is the standard, and 16 AWG allowed if the conditions of 240.4(D)(2) are met; I just looked up spec sheets on Square D & Eaton breaker, and the smallest acceptable conductor size is 14 AWG. I don't know if its a matter of changing the label, or if there will need to be a physical change to the lug.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I have a long way to go on reading through it all, but here are a few of my thoughts on what I've read so far.

1) 90.2(D)(5) has specified the NEC doesn't cover utility installations.
installations under exclusive control of electrical utility where such installation … consist of service drops or service laterals, and associated metering, or…

About 2-3 months ago, I had confrontation with an inspector who failed my installation due to not liking the way the utility wired their CT metering equipment. I explained it wasn't within his jurisdiction, he blew up, I then blew up, it was ugly. But glad to see they've added this.


This is an interesting change... I guess they're trying to clarify something, but using equally ambiguous terms.
110.12 - Electrical equipment shall be installed in a neat professional and workmanlike skillful manner.


Let's talk about this one.....
210.6 Branch Circuit Voltage Limitations- (A) Occupancy Limitation
In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following:
(1) Luminaires
(2) cord-and-plug connected loads 1440 volt-amperes, nominal, or less than 1/4 hp.

Who is going to police the cord-and-plug connected loads?

210.8 (GFCI's) has been expanded.

210.15 prohibits the use of reconditioned AFCI's. ---eyeroll---

210.18 adds the 10A circuit. Why? Lighting? Are we going to see 16/2 NM?
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
210.18 adds the 10A circuit. Why? Lighting? Are we going to see 16/2 NM?
I think were entering our second wave of aluminum taking over residential, last one was in the 70's.
Huge push by the Aluminum industry for copper clad aluminum 14/2 NM
Probably all manufactured homes and tract housing will be wired with copper-clad 14/2 and people wont even realize its aluminum.

We had a thread on the 10A circuits here:
Siemens at least have been making 10A breakers for a while, I have seen them in RV's, being a nerd I looked it up in the Speedfax and it was listed for 16 AWG conductors.

I think they should allow 16 AWG copper stranded NM and 16 TFFN also not just copperclad.
So add your public comments
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There is no real change in 90.2(D)(5). Utility installations, including the metering have been outside the scope of the NEC since before I started in 73.

210.6 is not a change...reads almost exactly the same in the 1999 code.

210.8. There is some expansion for other than dwelling units, but none for dwelling units.

10 amp circuits are to permit the use of 14 AWG copper clad aluminum. While there are 10 amp breakers and 10 amps has been added to the list of standard OCDP sizes in 240.6, there are no 10 amp AFCI breakers, so will not be able to use 10 amp circuits in most parts of a dwelling unit.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
10 amp circuits are to permit the use of 14 AWG copper clad aluminum. While there are 10 amp breakers and 10 amps has been added to the list of standard OCDP sizes in 240.6, there are no 10 amp AFCI breakers, so will not be able to use 10 amp circuits in most parts of a dwelling unit.
I dont see anything prohibiting 16 AWG copper if the conditions of 240.4(D)(2) are met.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
First Revision No. 8371-NFPA 70-2021 [ Section No. 310.3(A) ]
(A) Minimum Size of Conductors.
The minimum size of conductors for voltage ratings up to and including 2000 volts shall be 14
AWG copper or 12 AWG aluminum or copper 16 AWG copper, 14 AWG copper -clad
aluminum, or 12 AWG aluminum , except as permitted elsewhere in this Code.
 