For the 2023 NEC and the 2026 NEC I submitted various PIs to expand the allowances in 705.12(B) on load side interconnections in ways that will not overload the panelboard bus, but which do not fit into any of the existing categories. All of them have been rejected; I think the primary reason has been, to paraphrase, "705.12(B) is complicated enough, let's not add further language for corner cases."
However, this time around the CMP basically said "we see what you are trying to do, and it makes sense, but if you want to do that, just use 705.12(B)(6)." So those of you who are engineers [or who can get an engineer to sign off on the design under 2023 NEC 705.12(B)(6), aka 2020 NEC 705.12(B)(5)], can do any of the following:
1) Use a panelboard with at most 3 busbar connections, each of which is protected at the busbar ampacity. [Of course, you can do the same thing with a feeder interconnection with 705.12(A), so it's silly that to use a busbar instead of a wire-type feeder you need engineering supervision.]
2) Ignore one breaker of the smallest size present when applying 705.12(B)(3). So you can add one breaker for monitoring equipment or whatever to your combiner panels, as long as that breaker is not larger than any other breaker present. This is due to a counting argument--the extra breaker can be either a load or a source, but not both, so if you do the accounting "current in = current out" there's no way to get both sides to exceed the busbar rating due to one extra breaker not larger than any other breaker.
3) When you know what is connected to each breaker, label each breaker "source only," "load only," or "source or load." Then as long as the sum of all the sources, or the sum of all the loads, is no more than the busbar ampacity, you know the busbar can't be overloaded.
4) Take advantage of a 100% rated OCPD. E.g. if you have a PV-only service entrance with a 200A 100% rated service disconnect/OCPD, then you can connect that to a 200A MLO panel (all such are rated for 200A continuously) connected to (5) 50A breakers, each connected to an inverter with a maximum inverter output current of 40A.
Cheers, Wayne
However, this time around the CMP basically said "we see what you are trying to do, and it makes sense, but if you want to do that, just use 705.12(B)(6)." So those of you who are engineers [or who can get an engineer to sign off on the design under 2023 NEC 705.12(B)(6), aka 2020 NEC 705.12(B)(5)], can do any of the following:
1) Use a panelboard with at most 3 busbar connections, each of which is protected at the busbar ampacity. [Of course, you can do the same thing with a feeder interconnection with 705.12(A), so it's silly that to use a busbar instead of a wire-type feeder you need engineering supervision.]
2) Ignore one breaker of the smallest size present when applying 705.12(B)(3). So you can add one breaker for monitoring equipment or whatever to your combiner panels, as long as that breaker is not larger than any other breaker present. This is due to a counting argument--the extra breaker can be either a load or a source, but not both, so if you do the accounting "current in = current out" there's no way to get both sides to exceed the busbar rating due to one extra breaker not larger than any other breaker.
3) When you know what is connected to each breaker, label each breaker "source only," "load only," or "source or load." Then as long as the sum of all the sources, or the sum of all the loads, is no more than the busbar ampacity, you know the busbar can't be overloaded.
4) Take advantage of a 100% rated OCPD. E.g. if you have a PV-only service entrance with a 200A 100% rated service disconnect/OCPD, then you can connect that to a 200A MLO panel (all such are rated for 200A continuously) connected to (5) 50A breakers, each connected to an inverter with a maximum inverter output current of 40A.
Cheers, Wayne