2026 NEC MN-B Cable Changes

trevorm

Member
Location
Central Washington
Occupation
Electrician
Our Washington codes (WAC) just adopted some very intersting changes with regard to NM-B cable ampacity:
080 Ampacity of Types NM and NMC cable carrying suffix letter "-B".
(8)(a) The ampacity of Types NM and NMC cable carrying suffix letter "-B" shall be determined in accordance with NEC 310.14.
(b) The ampacity of #10 AWG and smaller ungrounded conductors shall not exceed that of a 60°C (140°F) rated conductor.
(c) The ampacity of ungrounded conductors larger than #10 AWG shall not exceed that of a 75°C (167°F) rated conductor.


You can view the actual code here

So it appears we (at least in Washington) can now use the 75 degree column for NM-B cable ampacity for conductors larger than #10awg. My 2026 copy of the NEC is enroute in the mail. Now anyone that already has a copy can you confirm this change has been made in the NEC as well? This rule change in the Washington code was approved in December 2025 along with the adoption of the 2026 NEC.
 
Our Washington codes (WAC) just adopted some very intersting changes with regard to NM-B cable ampacity:
080 Ampacity of Types NM and NMC cable carrying suffix letter "-B".
(8)(a) The ampacity of Types NM and NMC cable carrying suffix letter "-B" shall be determined in accordance with NEC 310.14.
(b) The ampacity of #10 AWG and smaller ungrounded conductors shall not exceed that of a 60°C (140°F) rated conductor.
(c) The ampacity of ungrounded conductors larger than #10 AWG shall not exceed that of a 75°C (167°F) rated conductor.


You can view the actual code here

So it appears we (at least in Washington) can now use the 75 degree column for NM-B cable ampacity for conductors larger than #10awg. My 2026 copy of the NEC is enroute in the mail. Now anyone that already has a copy can you confirm this change has been made in the NEC as well? This rule change in the Washington code was approved in December 2025 along with the adoption of the 2026 NEC.
No change in the 2026 NEC

(A) General

The ampacity of Types NM and NMC cable shall be determined in accordance with 310.14. The ampacity shall not exceed that of a 60°C (140°F) rated conductor. The 90°C (194°F) rating shall be permitted to be used for ampacity adjustment and correction calculations, provided the final calculated ampacity does not exceed that of a 60°C (140°F) rated conductor. The ampacity of Types NM and NMC cable installed in cable trays shall be determined in accordance with 392.80(A).
 
I welcome the change, being able to use the 75 degree column for nm-b #8 and #6 will be very helpful in some situations. I thought that state codes were supposed to be stricter than the NEC not relaxed such as in this case? Will be interesting how the local inspectors treat this since the NEC contradicts the State code.
 
WA has made many changes in the past to its Washington Administrative Code WAC 296-46B that ended up in the NEC. I was on many WAC code change committees and it’s a good process with inputs all across the industry. The final approval is by the electrical board, the chief electrical inspector is a non voting member. Currently stakeholders are being asked to apply to the committee for the 2026 code adoption.
In WA the WAC supersedes the NEC
 
I welcome the change, being able to use the 75 degree column for nm-b #8 and #6 will be very helpful in some situations. I thought that state codes were supposed to be stricter than the NEC not relaxed such as in this case? Will be interesting how the local inspectors treat this since the NEC contradicts the State code.


The NEC is a “Model Code”. You or I can write a model code as well. No state, county, city, or other public entities, is required to adopt any code, and if they do, they may adopt as much or as little as they please, and amend it as they see fit.


They can cut portions out, add sections, or rewrite entire portions if they wish to.

The NEC has zero force until and unless it is adopted by a local Authority Having Jurisdiction, whether that is state, county, city, whomever.
 
I welcome the change, being able to use the 75 degree column for nm-b #8 and #6 will be very helpful in some situations. I thought that state codes were supposed to be stricter than the NEC not relaxed such as in this case? Will be interesting how the local inspectors treat this since the NEC contradicts the State code.
States can adopt whatever they want and make whatever amendments they want. Many amendments actually are less strict than what is in NEC. Possibly there are more that are less strict than number of amendments that are more strict.

Some states possibly have rules that local jurisdictions can not lessen restrictions to any more than what the state rules are.
 
The NEC needs to ditch the completely stupid 60°C rating nonsense.
Is this influenced by steel tubing industry or electrical labor unions by any chance?

They don't directly write code but they certainly do research and presentations to try to sway code makers to see things their way just like many other organizations do (I won't mention the AFCI manufacturers, oops)
 
Is this influenced by steel tubing industry or electrical labor unions by any chance?

They don't directly write code but they certainly do research and presentations to try to sway code makers to see things their way just like many other organizations do (I won't mention the AFCI manufacturers, oops)
I don't think that labor unions care if NM cable can only be used as a 60°C conductor. I thinking that there have probably been dozens of PI's to bring NM cable up to 75°C since it contains 90° C conductors. The 60°C limit is nonsense given that it is required be constructed with conductors rated for 90° C.
 