2029 PI: 110.14(C) Number 2

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Change:

110.14(C) (1) Equipment Provisions.
The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or 110.14(C)(1)(b). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on the values from Table 310.16 as appropriately modified by , or Table 310.12 where applicable, without the application of any adjustment or correction factors.

. . .


Substantiation:

The phrase "based on Table 310.16" suggests that all of Table 310.16 applies, including the footnotes calling for ampacity adjustment and correction. It also suggests that the table value may not be the final answer for the ampacity of termination provisions, and that further modification may be necessary, such as applying ampacity adjustment and correction factors.

However, neither of these is true. UL listing standards for equipment incorporate the numbers from Table 310.16 for sizing conductors for equipment testing, without any adjustment or correction factors. And any deviation from that rule is covered by the initial phrase in this sentence of 110.14(C).

Changing the text of 110.14(C) to directly reference the values of Table 310.16 without correction or adjustment will thus increase clarity.
 