This one's for @tortuga.
Change:
430.62(A) Specific Load.
A feeder supplyinga specific only fixed motor load(s) and consisting of conductor sizes in accordance with 430.24 shall be provided with a protective device having a rating or setting not greater than the largest rating or setting of the branch-circuit short-circuit and ground-fault protective device for any motor supplied by the feeder [based on the maximum permitted value for the specific type of protective device in accordance with 430.52, or 440.22(A) for hermetic refrigerant motor-compressors], plus the sum of the full-load currents of the other motors of the group.
. . .
Substantiation:
Improve clarity by explicitly stating that 430.62 only applies to feeders that supply only motor loads. 430.63 covers feeders supplying mixed loads.
Change:
430.62(A) Specific Load.
A feeder supplying
. . .
Substantiation:
Improve clarity by explicitly stating that 430.62 only applies to feeders that supply only motor loads. 430.63 covers feeders supplying mixed loads.