The motor is not three-phase
Sent from my iPhone using Tapatalk
Very good...I stand corrected.
The motor is not three-phase
Sent from my iPhone using Tapatalk
Any call for OL trips usually means you will be investigating mechanical issues. You may not be the one that fixes the problem but until you can prove the problem is mechanical - the tripping OL is an electrical problem to the owner/operator.Reminds me of what a wise maintenance electrician once said
"Its always an electrical problem", meaning its never an electrical problem ...ie OL trip because the sewer pump is ragged up.
Some "air over" designed motors are built about same as a lower horsepower non air over rated motor, they just take advantage of the air flow to keep it cool enough to work in their intended applications.I was once told by an experienced guy who had rewound and rebuilt hundreds of motors that the biggest enemy of any motor was heat. Keep them cool and they will last forever.
That 30 years to 10 years is kind of dependent on duty and or abuse of the motor as well. Something that runs 24/7/365 is not going to last as long as something that runs 10 hours a day 5 days a week but is otherwise driving the same kind of load, or the same kind of load but one application the operator pushes it hard all the time and the other application they don't.Back when I was an apprentice in the 70s and underwent training on motor starters and maintenance, I was given what was called a "Horse Chart", depicting motors as "dumb horses" that will work themselves to death if allowed to. The idea was that it was our (electrician's) responsibility to be the Teamsters of the horses and not let them kill themselves in the performance of their duty. On that chart, they showed the effects of increasing the heater element size, with the horse getting sicker and sicker with each increase. As I recall, the rule of thumb was that for every size above what the motor nameplate FLA said, you cut the motor life by a factor of 3. So if a motor was designed to last 30 years under optimum conditions, bumping up the OL heater selection by one size cut that to 10 years, one more size; 3years, 3 sizes too big, under 1 year for a brand new motor.
I've never seen that chart again, but the closest I have found is a widely used axiom that says that for every 10deg. C above rated temperature that a motor operates, you cut the motor life in half.
This is absolutely a correct way to get a centrifugal pump to stay on line when it is overloaded. I would have to wonder exactly how it is piped, as typically you go into the filter, and then the heater after the pump discharge. There are a lot of untold problems with pump systems due to incorrect piping and or incorrect pump for the application.It is likely there is nothing wrong except that the pump does not have enough head on it and it is operating outside of its design curve. See it all the time on commercial pools. It just needs to have a throttling valve on the discharge of the pump to get the flow in line with the pump curve. You just throttle the flow back until the amperage is in line with the motor data plate. If then you do not have enough system flow the you have a design issue and the pump is to small.
It is likely there is nothing wrong except that the pump does not have enough head on it and it is operating outside of its design curve. See it all the time on commercial pools. It just needs to have a throttling valve on the discharge of the pump to get the flow in line with the pump curve. You just throttle the flow back until the amperage is in line with the motor data plate. If then you do not have enough system flow the you have a design issue and the pump is to small.