The 'Buck and Boost' transformer will give you correct line-line voltages, but will create a system with heavily unbalanced line to ground voltages.
This is often perfectly acceptable, for example supplying power to an 'across the line' started induction motor.
This can also be a big problem for some loads if there is a line-ground reference in the load. One common situation is when VFDs are used; the input to the VFD often has ground referenced transient voltage suppression, and this will be unhappy with anything other then a wye supply.
If the manufacturer has specifically given the okay to the use of the buck and boost transformer, then it should work just fine.
-Jon
This is often perfectly acceptable, for example supplying power to an 'across the line' started induction motor.
This can also be a big problem for some loads if there is a line-ground reference in the load. One common situation is when VFDs are used; the input to the VFD often has ground referenced transient voltage suppression, and this will be unhappy with anything other then a wye supply.
If the manufacturer has specifically given the okay to the use of the buck and boost transformer, then it should work just fine.
-Jon