Hi all,
Long time lurker, first time poster. I am hoping that the minds here can help me overcome a mental block.
I am trying to set up formulas to calculate power for various circuits in a data center. We have 208/120V power distribution panels from which we provide typically 208V circuits, usually L6 single-phase but sometimes 3 phase. The distribution panels have metering CTs on each pole measuring line current. All the equipment connected are single phase, typically 208V, servers.
For a simple L6 circuit, I know that power = V * A * Pf, so for a 24A load at .9pf, i get 208 * 24 * .9 = 4,492w.
For a balanced 3 phase circuit, power = V * A * 1.73 * Pf, so for the same 24A per line load I calculate 208 * 24 * 1.73 * .9 = 7,772w
But when I try to calculate the unbalanced load, I can't seem to make sense of it. Since the loads are effectively delta loads, a L6 circuit connected L1 - L2 should be the same power as a 3 phase circuit with all the loads on the L1 - L2 receptacle bank. My metering should still show 40A on L1 and L2 and 0A line 3. But my power calculation shows a consumption of 5,181w.
I'm sure there is some conceptual issue I am missing here. How can I fix the formulas or am I just missing a concept?
Thanks.
Thanks.