wire monk

Member
The bldg has 208 3 phase coming in , all the equipment furnace,water heater etc is 240 acording to the name plates single phase what's all the problems with the elements not heating up properly??
 

mdshunk

Senior Member
Location
Right here.
Just be advised that a lot of HVAC equipment designed for 240 has a jumper you can move at the low voltage transformer to do the control circuit better when served with 208.
 

neutral

Senior Member
Location
Missouri
Hi
Typical water heater
or other non inductive loads
E R I p

240 12.8 18.75 4500


208 12.8 16.25 3380


POWER AT REDUCED VOLTAGE 0.751111111 %

Charlie
 