The bldg has 208 3 phase coming in , all the equipment furnace,water heater etc is 240 acording to the name plates single phase what's all the problems with the elements not heating up properly??
 
Just be advised that a lot of HVAC equipment designed for 240 has a jumper you can move at the low voltage transformer to do the control circuit better when served with 208.
 
Hi
Typical water heater
or other non inductive loads
E R I p

240 12.8 18.75 4500


208 12.8 16.25 3380


POWER AT REDUCED VOLTAGE 0.751111111 %