synchro
- Chicago, IL
- EE
Got to remember that a modern autoclave is likely fully computerized, as such the power supply is very likely to have MOVs and many MOVs are rated 150v RMS MCOV. If it has a L1-G-L2 MOV and you consider the allowable continuous variation of +/- 5% and occasional allowance of up to +10%, you could have problems with cooking MOVs.
If the buck boost has two separate secondary windings each outputting 11V at a 208V input, then Larry's suggestion to wire one at each end of the primary will produce 129.6V L-G at both line outputs. Adding the +10% variation mentioned by Flicker Index would give 142.6V L-G.... If one needs a voltage boost that uses the series-connected secondaries, one could separate the two secondaries and wire one at each end of the primary, obtaining the boosted voltage while maintaining a balanced line-to-neutral output.
By comparison if 22V boost is applied at one end of the primary winding then a 10% increase above the 139.5V nominal would be 153.5V L-G . So Larry's idea is something to consider if the transformer allows it.