The SEC is an abbreviation for secondary.I'm not familiar with a an SEC transformer. I'm looking into it now but I'm pretty sure there are spaces for individual breakers for the independent loads.
Supply wires would have to land on a single ocpd (i.e. main; pedestal is MCB). If pedestals are MLO, perhaps a back-fed breaker can be set up as a main in each. [240.21(C)].... I'm looking into it now but I'm pretty sure there are spaces for individual breakers for the independent loads.
Look at any buck/boost diagram for 3?. Show me one that has a neutral for each 240V 1? connection, i.e. A-B, B-C, and C-A for balancing.I'm glad to finally quit just lurking here..been doing that for a few years now. But why does this situation need to be treated so particular? Once you have fed a 3 phase panel, you balance the loads the best you can with single & double pole breakers; with a little thought put into placement, it would seem you could do about as well as the average panel I usually see in a plant. The PDF appears to indicate that it can provide the correct voltages. I don't claim to know it will work, but it seems that it would.
Even if you came up with close to such a configuration, with three center taps, there is no way that you could ground them all.Look at any buck/boost diagram for 3?. Show me one that has a neutral for each 240V 1? connection, i.e. A-B, B-C, and C-A for balancing.
You can boost a 208Y/120 to a 240Y/138 with no problems. But there will be no 120/240 combination available (i.e. center tapped).I'm wondering if we are thinking of two separate things. Linked below is a drawing that shows a 3 phase, wye output with a common neutral as any other normal system. The 240 volt loads needing none, but one is there for all the single phase 120 loads. The balancing would be a bit of creative placement & luck of where the boats tie up. Here a link discusses their 3 phase wye buck/boost selection with wiring diagrams showing neutral in & out. There are no cautions on how to use or not use the 3 ph. wye feed. From the link below:
"Q4 Can I use a Buck-Boost Transformer to provide an output of 208Y/120 (or any other wye combination)?
A4. This all depends on your source. If you have a wye source, you can feed the wye through the autotransformer. If you have a High-Leg Delta or a 3-wire source, you can not create the wye for your application........."
I believe the 208/3 the OP mentioned would also have a neutral..
http://www.automationdirect.com/static/manuals/buckboosttransformer/buckboostmanual.pdf