Is it permissible to have 208 volt conductors and 4160 volt conductors run through the same pull box?
I think you meant 300.3(C)(2).See 300.2(C)(2)
Roger
Only if the installation meets one of the (a) through (e) conditions.So according to that section it's permitted.
Only if the installation meets one of the (a) through (e) conditions.
Roger
300.3(C)(2) Over 1000 Volts, Nominal. Conductors of circuitsrated over 1000 volts, nominal, shall not occupy the sameequipment wiring enclosure, cable, or raceway with conductorsof circuits rated 1000 volts, nominal, or less unlessotherwise permitted in 300.3(C)(2)(a) through (C)(2)(d).
(2) Over 600 Volts, Nominal. Conductors of circuits rated
over 600 volts, nominal, shall not occupy the same equipment
wiring enclosure, cable, or raceway with conductors
of circuits rated 600 volts, nominal, or less unless otherwise
permitted in (C)(2)(a) through (C)(2)(e).
I'm not seeing how those apply since pull box is not mentioned.
And I agree with both of you.The way this is written conductors of circuits over 600V cannot coexist with circuits under 600V in an equipment wiring enclosure, cable, or raceway, with the exceptions that follow.
Since a pull box is not an equipment wiring enclosure, cable, or raceway, it would appear to be acceptable.
ETA: must have changed it from 600V to 1000V in 2014 edition.
The way this is written conductors of circuits over 600V cannot coexist with circuits under 600V in an equipment wiring enclosure, cable, or raceway, with the exceptions that follow.
Since a pull box is not an equipment wiring enclosure, cable, or raceway, it would appear to be acceptable.
ETA: must have changed it from 600V to 1000V in 2014 edition.
And I agree with both of you.
Roger
NYC Code Amendments
ARTICLE 300 Wiring Methods
SECTION 300.3
Subsection 300.3(C)(1)(a) – Add a new subsection 300.3(C)(1)(a) to read as follows:
a) Barriers shall be provided to isolate conductors energized from different sources when system voltage exceeds 250 volts nominal and conductors are protected by first or second level overcurrent protective devices. Sources include service entrance points, secondaries of different transformers,generators and UPS systems.
Any idea what first or second level OCPD devices are?
Ground-fault protection is handled similarly in larger health care facilities. These facilities require two levels of protection, the main service overcurrent protective device (OCPD) and the second level OCPD to assure a feeder breaker opens on a fault condition prior to tripping the main circuit breaker.
So does this also apply to vaults which MDP's sit upon -- you seem to be stating that fused & unfused may occupy the same gutter (pull box) without separation
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable in which the service conductors are installed.
I don't think a pull box would be considered a racewayI believe the definition of raceway in the code would include both conduit and pull box. Thus this would not be permitted.
Raceway. An enclosed channel of metallic or nonmetallic
materials designed expressly for holding wires, cables, or busbars,
with additional functions as permitted in this Code.
A pull box would not be a raceway.
I don't think a pull box would be considered a raceway
I agree definitely not a raceway.