There was an attempt to add handholes in 2011. It was unanimously rejected.
2011 ROP
3-16 Log #1244 NEC-P03 Final Action: Reject
(300.3(C)(2)(e))
_______________________________________________________________
Submitter: Dan Leaf, Seneca, SC
Recommendation: Revise text as follows:
In handholes and manholes if the conductors of each system are permanently
and effectively separated from the conductors of the other system. and Where
installed in manholes conductors shall be securely supported and fastened to
racks insulators, or other approved supports. Conductor of different voltage
rating shall be permitted.
Conductors having nonshielded insulation and operating at different voltage
levels shall not occupy the same enclosure, cable, or raceway unless they
comply with 300.3(C)(2)(e).
Substantiation: Handholes should be included. Racks, insulators and supports
should not be necessary for handholes. Proposed deletion is superfluous, this
subsection concerns circuit ratings, not conductor ratings. Section 300.3 should
be referenced.
Panel Meeting Action: Reject
Panel Statement: Providing permanent and effective separation of 600-volt or
less from over 600-volt conductors within a handhole would be very difficult,
if not impossible. The submitter should provide additional technical
substantiation and data showing handholes and the method of providing
permanent and effective separation.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14
_______________________________________________________________
2011 ROP
3-16 Log #1244 NEC-P03 Final Action: Reject
(300.3(C)(2)(e))
_______________________________________________________________
Submitter: Dan Leaf, Seneca, SC
Recommendation: Revise text as follows:
In handholes and manholes if the conductors of each system are permanently
and effectively separated from the conductors of the other system. and Where
installed in manholes conductors shall be securely supported and fastened to
racks insulators, or other approved supports. Conductor of different voltage
rating shall be permitted.
Conductors having nonshielded insulation and operating at different voltage
levels shall not occupy the same enclosure, cable, or raceway unless they
comply with 300.3(C)(2)(e).
Substantiation: Handholes should be included. Racks, insulators and supports
should not be necessary for handholes. Proposed deletion is superfluous, this
subsection concerns circuit ratings, not conductor ratings. Section 300.3 should
be referenced.
Panel Meeting Action: Reject
Panel Statement: Providing permanent and effective separation of 600-volt or
less from over 600-volt conductors within a handhole would be very difficult,
if not impossible. The submitter should provide additional technical
substantiation and data showing handholes and the method of providing
permanent and effective separation.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14
_______________________________________________________________