If you have full delta with all three sides of equal capacity, it may be desirable to utilize all three phases with certain loads to help balance the system.No matter how you slice it, don't use the "high leg" for single phase loads; just don't. If you have a 208/240v load, use the two main legs for 240v; if you must have 208v for some equipment, use a buck transformer.
Jreaf- I tend to agree, but SDSs could fight for the title.
You could even have say some lower capacity 240 volt heaters but several of them balanced across all three phases, maybe even on one circuit with a three pole breaker.