Hello All,
This topic has been gone over a few times on this forum but I just wanted to display the question in a different form:
For a 10KVA 2 pole single phase load on a 208V/120V system, what is the per phase current?
When doing a panel schedule I would split the 10KVA between the two phases so I would have 5KVA on each phase, then I would do the same for all other loads, distributing them as required whether 120V loads, 208V Single phase loads, or 3 phase 208V loads. I then get the per phase current by taking the column for each phases summed up KVA and dividing by 120V.
However, how do we get around the discrepancy when looking at one load:
208V, 2 Pole load, 10KVA:
10KVA/208V = 48.08A
5KVA/120V = 41.67A
Its close, but not close enough to be sufficiently the same. Is it just a limitation of the assumptions/simplifications we make when trying to do a panel schedule and utilizing loads that should be 100% balanced but are not?
This topic has been gone over a few times on this forum but I just wanted to display the question in a different form:
For a 10KVA 2 pole single phase load on a 208V/120V system, what is the per phase current?
When doing a panel schedule I would split the 10KVA between the two phases so I would have 5KVA on each phase, then I would do the same for all other loads, distributing them as required whether 120V loads, 208V Single phase loads, or 3 phase 208V loads. I then get the per phase current by taking the column for each phases summed up KVA and dividing by 120V.
However, how do we get around the discrepancy when looking at one load:
208V, 2 Pole load, 10KVA:
10KVA/208V = 48.08A
5KVA/120V = 41.67A
Its close, but not close enough to be sufficiently the same. Is it just a limitation of the assumptions/simplifications we make when trying to do a panel schedule and utilizing loads that should be 100% balanced but are not?