wasasparky
Senior Member
When determining amps for 208V motor loads, which column do you use?
200V, correct?
If so, what is the 208V column for?
200V, correct?
If so, what is the 208V column for?
charlie b said:I would use the 208V column, and be left wondering why the 200V column exists. :-?
wasasparky said:What about 460V column for 480V systems.
What about 230V column for 240V systems.
etc.
rbalex said:I would accept the 204A answer as the ?basic? answer and 199A as the ?engineered? answer.
rbalex said:I said your second METHOD was accurate because it accounts for the 30 degree phase shift between the 208 three-phase motor (and 120 single-phase) currents and the 208 single-phase currents. .[/FONT]