dnem said:That's what I was thinking
I wasn't thinking that. . But now that I've read it a few times, it's sinking in ..... kinda.
"Ztotal = 1.5/2 that of a full winding."
So Z is low because of the two paths from highleg to neutral. . Are you saying this is a disadvantage or a problem ? . Is "weak source impedance" a bad thing ? . It sounds like a good thing to me.
"For a resistive load, Ibn carries a phase angle of 90 degrees which is 90 degrees out of phase from Van and Vbn and 30 degrees out from Vba and Vbc."
So does this mean alot of wasted power because of the 90? out of phase ?
So besides the usual losses, you take an additional "hit" because of the phase angle differences of 2 series phases that are out of phase with each other ? . Impedance in the source transformer, impedance in the load motor, resistance thruout the entire circuit plus this additional loss ? . In addition to the usual losses, you would still need 115.4va in the secondary to deliver 100w at the load ?
Am I seeing the issue here ?
I would say that the 120V legs are providing apparent power (VA) but no real power (W). This current still loads transformer A-C. The other phases would be providing power at angles of +/- 30 degrees.
In short it appears that even moderate use of the wild leg would make it difficult to balance the load as well as making poor use of the transformer ratings.
Furthermore, all this current would flow in the neutral--not good.