rattus said:
The attached diagram shows the qualitative effects of series resistance and leakage inductance on Vbn in a wild leg service with no other loading. It looks strange, but I do believe it is correct.
The load current is assumed to carry a phase angle of 90 degrees.
Comments welcomed.
Well, I crunched some numbers for fun.
I'm not too happy to see one of the 120 volt legs increase and one decrease as it is not what I would have guessed, but I do not feel like re-drawing the diagram right now.
Just wondering if the numbers even make sense. If no one feels like tackling a similar calc, I'll re-calc my numbers later, maybe on the computer instead of paper to avoid calculator key-punch errors.
I assumed some reasonable %Z and %R for a 3-pot wye-delta bank and transfered everything to the load-side. I also assumed a neutral reference (don't have a cow carl), with the reference voltages of 120<180, 120<0, 207.8<90
With a resistance such that the high leg load was close to rated per-phase current: 116.1<180.79, 123.9<-0.74, 203.4<86.72 and IR = 94% FLC
With an impedance such that the high leg load was close to rated per-phase current: 121.3<-181.82, 118.8<-1.86, 196.3<91.09 and IZ = 91% FLC