20A minimum CB

Status
Not open for further replies.

lizzie14

Member
I heard that somewhere in the code the minimum cb size you can use is a 20A. Does anyone know if this is for strictly commercial or residential?? Does anyone know where it states that?
 
Re: 20A minimum CB

You can use a micro amp circuit breaker if you so desired to spend the money to have one made. The NEC does not have a minimum OCPD requirement.

Roger
 
Re: 20A minimum CB

For UL489 devices the minimum is 15a. Even though there are some 10a rated devices of the same frame size I'm not aware that there any that are available with a UL489 listed.
Reference 240.6 Standard Ampere ratings.
There are UL1077 supplementary protectors for a wide range of amp ratings available but they must be applied per 240.10 and are not to considered as a substitute for branch circuit over-current protection. The are available in ampacities in a range of .5a to about 60a. However, they are different than the UL489 devices in that they are often available with a choice of at least 2 time/current trip curves.
Again, they can not be used as a subsitute for a UL489 listed device.
 
Re: 20A minimum CB

Even a 10 amp breaker as unordinary as the QO210SWN (switched neutral) is UL489 listed.

Roger
 
Re: 20A minimum CB

15 amps is the smallest standard circuit breaker - 240.6(A). 20A would only be a minimum size if the load is continuous, and greater than 12 Amps.

Steve
 
Re: 20A minimum CB

Yes, I did notice that not only SqD but C-H has UL489 listed 10a breakers available which were not a number of years ago. But other than being used within UL listed assemblies I can't see how they would be applied within the NEC requirements even though there may even be a few other ratings that are UL listed that are not included in the standard ratings in the NEC.
 
Re: 20A minimum CB

Originally posted by templdl:
But other than being used within UL listed assemblies I can't see how they would be applied within the NEC requirements even though there may even be a few other ratings that are UL listed that are not included in the standard ratings in the NEC.
The last sentence of 240.6 would allow fuses and inverse time circuit breakers with" nonstandard" ampere ratings to be used anywhere it would be practicle or desired for a specific circuit .

Roger
 
Re: 20A minimum CB

Roger, that covers it all right. But, if one were to specifically consider branch circuit protection using rated wire were would a 10a rated breaker be applied seeing that #14 wire is the smallest wire included on table 310.16?
 
Re: 20A minimum CB

Would these be for de-rating conductors due to 310.15B2a or high ambient conditions??? For 14 gauge, that would be more than 9 in 1 conduit, for 12 gauge, that would be 21 or more in 1 conduit... do you need to limit only the load, or the breaker and the load?

I HAVE seen one 10A QO used as a supply to a transformer that powered a load sequencer in a panel for a theater audio system. The unit is built in to a connected box to the side of a QO load center, and uses _motorized_ QO breakers(don't see many of those!) to sequence the loads when you push a Start/Stop station.

There are pictures, etc at this site.

Mike
 