Not to pile it on here- but even if there was a full 20 amps on that ckt, the #14 would very likely safely handle that load indefinitely.
Violation, sure (in most cases....). Imminent danger, no.
The amperage tables were designed with a cushion in mind- which FTR, I see nothing wrong with.
You beat me to it. #14 is not going to melt down or get damaged by 20 amps of load. In fact, the ampacity table used to list #14 as being suitable for 20 amps before it was revised.