Re: 20amp 2pole on 12/3 wire
Originally posted by Joe the Rugg:
Yoke in the electrical handbook is described as that little break off tab on a receptacle.
What handbook says that?
I have never heard that and believe that is incorrect.
In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
This could be a two pole breaker, a listed handle tie across two single pole breakers or IMO even a two pole switch at the panel board.
My background is in commerical, where one neutral for 3 hots but we don't put them on a 3pole breaker.
There are times even in commercial that handle ties are required for multiwire branch circuits.
210.4(B) (2005 NEC) this is a change from 2002 it now applies to all occupancies.
Also check out 210.7 (2002 or 2005 NEC) for multiple circuits feeding a single yoke or strap
Multiwire circuits feeding office cubicles are now required to have handle ties. 605.6 or 605.7 2005 NEC.