In a new critical facility I have a 120V 20KVA UPS (which I can only load to 18kVA) which feeds (4) 120V-1P panels. These panels serve 120V lighting and receptacles. I'm trying to figure out how much load I can put on each panel.
Customer requires only loading to 80% = 18kVA or 150A at 120V.
This gives 150/4=37.5A per panel. Is this correct thinking?
180VA/receptacle
the lighting is on 24/7 and desktop computers are, too. Don't know how many will actually be plugged in. So the lighting is continous and some of the rcpt loads are.