caosesvida

Senior Member
(21 amps on each leg) 440, three phase heater,
21 * 440 * 1.73 = 15985 watts . is this correct? There is no power factor on pure resistance loads, right? thanks
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: 21 amp three phase heater

For three-phase W= E x I x PF x 1.73 Go figure. Hint PF = 1 on pure resistive load.

[ January 30, 2004, 02:05 PM: Message edited by: dereckbc ]
 

gazzoo

Member
Re: 21 amp three phase heater

Originally posted by caosesvida:
(21 amps on each leg) 440, three phase heater,
21 * 440 * 1.73 = 15985 watts . is this correct? There is no power factor on pure resistance loads, right? thanks
No, your ANSWER TOTAL is not correct. PF=1 on a purely resistive load. Once you get the right answer try to find the resistance on the load post back with the resistance total. Have fun!

 

bob

Senior Member
Location
Alabama
Re: 21 amp three phase heater

(21 amps on each leg) 440, three phase heater,
21 * 440 * 1.73 = 15985 watts . is this correct? There is no power factor on pure resistance loads, right? thanks
If the voltage is truley 440 volts, your answer looks correct to me. There is a power factor involved. It just happens to be 1 or unity.
 