(21 amps on each leg) 440, three phase heater,
21 * 440 * 1.73 = 15985 watts . is this correct? There is no power factor on pure resistance loads, right? thanks
Re: 21 amp three phase heater
For three-phase W= E x I x PF x 1.73 Go figure. Hint PF = 1 on pure resistive load.
[ January 30, 2004, 02:05 PM: Message edited by: dereckbc ]
No, your ANSWER TOTAL is not correct. PF=1 on a purely resistive load. Once you get the right answer try to find the resistance on the load post back with the resistance total. Have fun!
If the voltage is truley 440 volts, your answer looks correct to me. There is a power factor involved. It just happens to be 1 or unity.