radiopet
Senior Member
- Location
- Spotsylvania, VA
Hey Guys,
I was reading some old posts while working on a lesson for a CEU program i am working on and came across an interesting debate between M.D. and a few others on the intent of 210.11(C)(3)....
This question was asked and answered the IAEI.
Q: Does the NEC allow any receptacles in a bathroom to be on a 15-ampere circuit" The homeowner wants a lighting receptacle to plug in rope lights as a night-light. The 15-ampere receptacle would be GFCI protected and in addition to the required 20-ampere receptacle circuit.
ANS: Yes, this would be allowed. Section 210.11(C)(3) of the NEC states, "In addition to the number of branch circuit required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets." While the 20-ampere branch circuit is required additional circuits or outlets are not prohibited.
yeah....the post was from last year but found it interesting anyway...
I was reading some old posts while working on a lesson for a CEU program i am working on and came across an interesting debate between M.D. and a few others on the intent of 210.11(C)(3)....
This question was asked and answered the IAEI.
Q: Does the NEC allow any receptacles in a bathroom to be on a 15-ampere circuit" The homeowner wants a lighting receptacle to plug in rope lights as a night-light. The 15-ampere receptacle would be GFCI protected and in addition to the required 20-ampere receptacle circuit.
ANS: Yes, this would be allowed. Section 210.11(C)(3) of the NEC states, "In addition to the number of branch circuit required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets." While the 20-ampere branch circuit is required additional circuits or outlets are not prohibited.
yeah....the post was from last year but found it interesting anyway...