I design industrial machinery, not outlets, but I was wondering if when I size a voltage drop could a JHA apply this rule to my machine ?
Example: I need 460 VAC 3P at 40 amps 1200 feet from the source. I would step the voltage to 560 VAC 3P and have 480 VAC 3P at 1200 feet. (Yes I would increase the Amperage to account for the loss in the step-up transformer and yes I would be sizing the step-up transformer supply wire at 4 AWG probably)
That is way more than the not to exceed 5%.
Thanks in advance
Mark Burnett
Example: I need 460 VAC 3P at 40 amps 1200 feet from the source. I would step the voltage to 560 VAC 3P and have 480 VAC 3P at 1200 feet. (Yes I would increase the Amperage to account for the loss in the step-up transformer and yes I would be sizing the step-up transformer supply wire at 4 AWG probably)