Re: 210.19(A)(3) Exception
The branch circuit tap conductors as per 210.19(A)(3)ex. are not really restricted by length such as in 240.21(B). If one is to run a 50 amp protected set of conductors to a junction box under the cabinet, and from that junction box run a set of 8 AWG to the wall oven,with another set of 10 AWG to a 30 amp cooktop, he would be able to. Either set of conductors leaving the junction box are permitted to extend to a location in the kitchen where the two different appliances are located. In this example, wall oven located against the wall, and the cooktop at the island. I do not see a problem with this installation. Maybe the size of the junction box...
The branch circuit tap conductors as per 210.19(A)(3)ex. are not really restricted by length such as in 240.21(B). If one is to run a 50 amp protected set of conductors to a junction box under the cabinet, and from that junction box run a set of 8 AWG to the wall oven,with another set of 10 AWG to a 30 amp cooktop, he would be able to. Either set of conductors leaving the junction box are permitted to extend to a location in the kitchen where the two different appliances are located. In this example, wall oven located against the wall, and the cooktop at the island. I do not see a problem with this installation. Maybe the size of the junction box...