210.19(A)(3) - Range Demand Load

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Hospital Master Electrician
1.) NEC Section/Paragraph: 210.19(A)(3)
2.) Proposal/Comment Recommends: [new text]
3.) Proposal/Comment: Add the following to the end of 210.19(A)(3):

The demand load as calculated in accordance with Article 220 shall be permitted as the maximum load to be served.

4.) Substantiation: Table 220.55, note 4, allows the branch circuit load to be derived from the table. This would clarify the use of the table at the branch circuit level. As this section reads, it could be interpreted two ways; one by the nameplate of the appliance, and the other by Table 220.55 as allowed by that section.
 