I want to make sure I am applying this exception correctly.  If I have a 60 amp continuous load, with 75 degree terminations at the breaker, the load and using 75 degree conductor(110.14 C),  125% of 60 is 75 amps requiring #4 conductor (85 amps) and an 80 amp breaker (240.4(b)).  The grounded conductor of this 120 volt single phase to neutral would only need to be a number 6?  Where in branch circuits does it state that the grounded conductor is not protected by the OCPD? If it is protected, what kind of protection is it? Is a branch circuit only the ungrounded conductors? The definition of branch circuit seems to leave this as a possibility.  Thank you.
	
		
			
		
		
	
				
			
				