Was asked the following question today and like to pass these on to the forum
210.20(A) states the maximum load on a overcurrent device is 125% of the continuous loads plus 100% of the non continuous loads
Commonly its stated that you can never load a branch circuit to more than 80% of the overcurrent device rating (80% is the inverse of 125%)
Does this mean for non continuous loads the overcurrent device can be loaded to 100%?