210.25 as it applies to Dorm. Dwelling Unit

Status
Not open for further replies.

Designer69

Senior Member
210.25 says that branch circuits from a dwelling unit shall supply only loads within that dwelling unit.

Well this dwelling unit has 2 means of egress and qualifies for emergency egress lighting (as far as I can make sense of the bldg code).

I just want to make sure that I can still bring in an emergency circuit from outside the dwelling unit (basement where emerg. panel is) into the dwelling unit for the emerg. egress lights and that this is ok.

This is a dormitory setup type building, with only one meter for the building, but the dwelling unit/apartment is separated from the other "boarding" areas and has its own panelboard.

Thank you
 
210.25 says that branch circuits from a dwelling unit shall supply only loads within that dwelling unit.

Well this dwelling unit has 2 means of egress and qualifies for emergency egress lighting (as far as I can make sense of the bldg code).

I just want to make sure that I can still bring in an emergency circuit from outside the dwelling unit (basement where emerg. panel is) into the dwelling unit for the emerg. egress lights and that this is ok.

This is a dormitory setup type building, with only one meter for the building, but the dwelling unit/apartment is separated from the other "boarding" areas and has its own panelboard.

Thank you

Does this dorm room actually meet the NEC definition of "dwelling unit"?
 
Yes I would say it does.

View attachment 20357

More details are needed. In my state "permanent provisions for cooking" means a range or a permanent cook top. Microwaves are not considered as permanent provisions for cooking. A shared bathroom may also change things as then it may not be considered a "single unit" or "independent". A call to the AHJ may be helpful.
 
Last edited:
yes it is definitely a dwelling unit, with electric range and all.

So going back to the initial question... is it allowable to run an emerg. circuit from the basement emerg. panelboard into this dwelling unit to supply the emerg. egress lights and without violating 210.25?


I would think this is acceptable sinc 210.25 only seems to require not supplying outside loads from the dwelling unit, but not vise versa.

Just want to make sure I'm not misinterpreting.
 
yes it is definitely a dwelling unit, with electric range and all.

So going back to the initial question... is it allowable to run an emerg. circuit from the basement emerg. panelboard into this dwelling unit to supply the emerg. egress lights and without violating 210.25?


I would think this is acceptable sinc 210.25 only seems to require not supplying outside loads from the dwelling unit, but not vise versa.

Just want to make sure I'm not misinterpreting.
That is how I see it

210.25 says that branch circuits from a dwelling unit shall supply only loads within that dwelling unit.
Plus it is also followed with

or loads associated only with that dwelling unit.

Your "emergency circuit" is likely associated with more then just loads in "that dwelling unit".
 
That is how I see it

Plus it is also followed with



Your "emergency circuit" is likely associated with more then just loads in "that dwelling unit".

It doesn't say "from each dwelling unit" it says "in each dwelling unit". IMO this does not mean that you cannot supply the EM lights form a panel remote form the dwelling unit, but once that branch circuit enters the dwelling unit, you cannot supply other loads that are not in the dwelling unit or loads that are not associated with that dwelling unit with that branch circuit.

(A) Dwelling Unit Branch Circuits. Branch circuits in each
dwelling unit shall supply only loads within that dwelling unit
or loads associated only with that dwelling unit.
 
It doesn't say "from each dwelling unit" it says "in each dwelling unit". IMO this does not mean that you cannot supply the EM lights form a panel remote form the dwelling unit, but once that branch circuit enters the dwelling unit, you cannot supply other loads that are not in the dwelling unit or loads that are not associated with that dwelling unit with that branch circuit.

(A) Dwelling Unit Branch Circuits. Branch circuits in each
dwelling unit shall supply only loads within that dwelling unit
or loads associated only with that dwelling unit.
I quoted
210.25 says that branch circuits from a dwelling unit shall supply only loads within that dwelling unit.
from your OP and sort of missed that difference when reading from code.

Seem to have answered your own question now that you said that.

Unless someone finds other wording I think you need to run a feeder from emergency system to the dwelling unit and then install branch circuit off that to your egress lighting within the unit.
 
I quoted from your OP and sort of missed that difference when reading from code.

Seem to have answered your own question now that you said that.

Unless someone finds other wording I think you need to run a feeder from emergency system to the dwelling unit and then install branch circuit off that to your egress lighting within the unit.

I'm not the OP.
 