210.5

Stubby

Member
Location
Climax
Occupation
Electrical
I got turn down for not phasing my ungrounded conductors on load side of disconnect. Voltage 120/208 3ph He. noted 210.5C. I don't think that applies to the load side of the disconnect
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
You didn't say whether you have more than one voltage system in the building. 210.5C only applies to that or certain DC circuits.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If there is only one voltage system within the building as Strathead stated no phase identification is required. You said load side so the line side is identified?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I got turn down for not phasing my ungrounded conductors on load side of disconnect. Voltage 120/208 3ph He. noted 210.5C. I don't think that applies to the load side of the disconnect
If identification is required, it is required for all conductors of the circuit, including the load side of a disconnect.
 