I'm sure this has already been addressed but did not come up in a search or in FAQ. For the sake of calculating the total amount of receptacles needed for an island can I count a duplex receptacle as two outlets?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
For the purpose of counting max allowed receptacles NEC 605.9(C) defines 1 duplex as equivalent to 2 simplex.
 

realboss

Electrical Contractor
Location
Arizona
Occupation
Owner
I agree, it's also two receptacles so you have to look carefully at how the island requirement is worded.
Hence the reason I'm asking the question..... :):) Under the 2020NEC we have to calculate the sqf of the island slab to determine the amount of required receptacles. we are trying to determine if we can argue that we are installing 4 receptacles (duplex on each end) and not have to install a double duplex on one side.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is the 2020
(2) Island and Peninsular Countertops and Work Surfaces.

Receptacle outlets shall be installed in accordance with 210.52(C)(2)(a) and (C)(2)(b).
  • (a)
    At least one receptacle outlet shall be provided for the first 0.84 m2 (9 ft2), or fraction thereof, of the countertop or work surface. A receptacle outlet shall be provided for every additional 1.7 m2 (18 ft2), or fraction thereof, of the countertop or work surface.
  • (b)
    At least one receptacle outlet shall be located within 600 mm (2 ft) of the outer end of a peninsular countertop or work surface. Additional required receptacle outlets shall be permitted to be located as determined by the installer, designer, or building owner. The location of the receptacle outlets shall be in accordance with 210.52(C)(3).

A peninsular countertop shall be measured from the connected perpendicular wall.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Hence the reason I'm asking the question..... :):) Under the 2020NEC we have to calculate the sqf of the island slab to determine the amount of required receptacles. we are trying to determine if we can argue that we are installing 4 receptacles (duplex on each end) and not have to install a double duplex on one side.
I don't have the 2020 with me but isn't the requirement for "receptacle outlets" not receptacles?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is the enhanced content

The general receptacle outlet requirement for qualifying island and peninsula countertop spaces in 210.52(C)(2) and (C)(3) calls for one receptacle outlet for the first 9 square feet, or 1296 square inches of countertop space. If the countertop is larger than 9 square feet, a second receptacle would be required for the next 18 square feet or 2592 square inches of the countertop space. If the countertop is larger, an additional receptacle would be required for every additional 18 square feet, or 2592 square inches, of countertop space. If the island or peninsula countertop is separated into two or more spaces, such as by a cooktop or a sink, and each space is at least 12 inches wide, the spaces would be treated as separate countertops and receptacle placement would be based on 210.52(C)(2). The receptacle outlet for a peninsula countertop is required to be located not further than 2 feet from the outer (the edge furthest from the connecting edge) edge of the peninsula countertop. Additional receptacles can be located at the discretion of the owner, installer, or designer. Unlike peninsula countertops, island countertops do not have a mandatory receptacle outlet placement requirement, and the minimum number of outlet(s) determined in accordance with 210.52(C)(2)(a) can all be located as desired by the owner, installer, or designer.
 