Which rendition is correct?
NEC 2017 210.52 (C) Countertops and Work Surfaces.(3) Peninsular Countertop Spaces. At least one receptacle outlet shall be installed at each peninsular countertop long dimension space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connected perpendicular wall.
I'm still not seeing that. I looked at both the code paragraph and the handbook commentary.
To me, it looks like a receptacle is required on the long dimension. That sounds like a receptacle on the side of the island. One on the counter top wall wouldn't work, and one on the end of the island wouldn't work.
I must still be missing something, because everyone else seems to agree with you.
I'm sure this will make it clear as mud -- "long dimension space" - "from the connected perpendicular wall." I had redrawn in the left illustration to match the wording in the 2017 NEC .
Therefore only 1 recept is required for the entire continuous pennisular in which the connecting point is the wall , the long dimesion is measured from wall to far end of the pennisular. According to the wording I would believe that the placement for the receptacle can be placed anywhere around the pennisular counter top & be compliant(end/front edge/wall/ back edge) as long as it is within NEC parameters.
You could have a case in which the first wall recept is 4' measured from the back side of the pennisular counter top along the wall. per the NEC wording.
The right illustration shows the connecting point at the wall front edge counter top which would require a recept for the wall counter top plus another for the pennisular, this is the illustration in the NEC 2017 handbook