210.52B and exhaust hood on small appliance ckt

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
IMO an exhaust hood should not be allowed on small appliance branch circuit thru 210.52B. Please feel free to correct me I have been wrong many times.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
You are correct.

No Other Outlets. The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no other
outlets.

-Hal
Thats how I read it i figured hood might be considered fixed in place appliance. If they had a 3rd 20amp circuit say for dining room could it go on that. IMO yes
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You also might want to take 422.16(B)(4) into consideration. If applicable to your installation, it requires a 20 amp individual circuit.
 

Buck Parrish

Senior Member
Location
NC & IN
We put the hood and the gas stove on the SABC for many years. It was not until recently we started to run all of them on a 20A dedicated circuit.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Augie, is that section only for cord and plug connected hoods?
Seemingly so and that was the reason for "if applicable". I was unsure if the OP had cord or hard wired but I wanted to make him aware of the Section.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
You also might want to take 422.16(B)(4) into consideration. If applicable to your installation, it requires a 20 amp individual circuit.
Thank you I see in B(4)(5) if using receptacle must have individual branch circuit
 