Thanks Dennis. I'm having a hard time with this one. I searched through this forum and read all 210.60(B) posts.
The part that bothers me is that the wording in this section is really not clear. Long story short, everyone has an opinion on 210.60(B) and they're all different.
Here's the wording 210.60(B):
"The total number of receptacle outlets shall not be less than required in
210.52(A). These receptacle outlets shall be permitted to be located conveniently for permanent furniture layout. At least two receptacle outlets shall be readily accessible. Where receptacles are installed behind the bed, the receptacle shall be located to prevent the bed from contacting any attachment plug that may be installed or the receptacle shall be provided with a suitable guard."
From the previous posts, some people are hanging their hat of the opinion that as long as you meet the minimum quantity of receptacles required in 210.52(A), then you don't have to adhere to the 6' / 12' receptacle spacing rules in dormitories, regardless of whether or not permanent furniture is installed at the locations requiring a receptacle. I don't interpret 210.60(B) that way but I can understand why some people are thinking that because this section is not clear. But using this logic, 6 duplex receptacles can all be installed within 24" of wall space and still meet the requirements in 210.60(B) - regardless of furniture placement?? This part makes no sense to me.
I'm of the opinion that 210.60(B) simply means that if you have permanent furniture blocking the 6' / 12' receptacle placement requirements in 210.52(A), then it gives you the allowances to adjust as necessary.
What exactly is the intent of 210.60(B) and why can't this section be written better.