I have a rehab from hell project happening....210.63
Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20- ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, airconditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to theload side of the equipment disconnecting means.
Exception:
A receptacle outlet shall not be required at one- and two-family dwellings for the service of evaporative coolers.
Questions:
1 - The AHU is located on it's side, under the "peaked/eave"(?) of the roof on this SFH Cape home, behind a knee wall, with an access panel, buried behind a closet....am I required to provide both a light and GFCI outlet ...just a GFI...just a light? (servicing)
2 - If a light is required....since it's not in a closet (behind it, through the access panel...) will a keyless suffice?
3 - What the heck is an "evaporative cooler"? (210.63 Exception) The only result from a search in the '05 was that exception???