This pretty much sums it up.210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
We can't allow a consensus here, it is just plain wrong.Originally posted by physis:
That , I think, qualifies as a concencus.![]()
This commentary may be left over from several code cycles ago where this requirement only applied to equipment outdoors, on rooftops, or attics.Originally posted by georgestolz:
Notice that the section itself doesn't say "outdoors."
Handbook commentary is commentary.![]()
Wouldn't that be "consensi", or perhaps "consensae"?Originally posted by physis:
Bob's right, consensusi () are forbidden.