Just noticed this, but in my 2020 NEC Handbook, under 210.70(A) Dwelling Units, lighting outlets installed according to 210.70(A)(1), (A)(2), and (A)(3). I don't have an (A)(3) in my handbook. According to the 2017 version, (A)(3) is Storage or Equipment Spaces. Just curious of what it is in others 2020 versions.
 
Just noticed this, but in my 2020 NEC Handbook, under 210.70(A) Dwelling Units, lighting outlets installed according to 210.70(A)(1), (A)(2), and (A)(3). I don't have an (A)(3) in my handbook. According to the 2017 version, (A)(3) is Storage or Equipment Spaces. Just curious of what it is in others 2020 versions.
Nope.
86f08c94626ef7a21c97594f42b7c768.jpg


Sent from my BE2028 using Tapatalk
 
The storage area lighting rules are in 210.70(C) in the 2020 code. They now apply to all occupancies and not just dwellings, so they had to be moved out of 210.70(A) which only applies to dwellings.
 