This is a question about what is / or should be required on a final residential inspection.
In a residential garage or basement, if I have a single plug by a sump pump or a duplex by a sump pump with a battery backup, I can easily see the dedicated space because the equipment is installed at the time of the final. But what about a situation where the equipment isn't installed at the time of final inspection and there are no electrical plans that show the equipment ?
Let me give you 3 examples, all of which I'm seeing in one development:
1) Empty garage with a single [in addition to a separate GFCI]. Square shaped garage with no cove areas that would be obvious for a dedicated space.
Is it enough for the contractor to verbally tell the inspector that a piece of equipment is coming at the time of move in ?
Is it reasonable for the inspector to ask that the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
2) Empty garage with a duplex [in addition to a separate GFCI]. Square shaped garage with no cove areas that would be obvious for a dedicated space.
Is it enough for the contractor to verbally tell the inspector that 2 pieces of equipment are coming at the time of move in ?
Is it reasonable for the inspector to ask that the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
3) Empty garage with a duplex. The required GFCI is loaded off of a basement GFCI so that one duplex is protected, the other is not, but visually there is no difference between the two plugs.
Is it enough for the contractor to verbally tell the inspector that 2 pieces of equipment are coming at the time of move in ?
Is it reasonable for the inspector to ask that the nonGFCI receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
David
In a residential garage or basement, if I have a single plug by a sump pump or a duplex by a sump pump with a battery backup, I can easily see the dedicated space because the equipment is installed at the time of the final. But what about a situation where the equipment isn't installed at the time of final inspection and there are no electrical plans that show the equipment ?
Let me give you 3 examples, all of which I'm seeing in one development:
1) Empty garage with a single [in addition to a separate GFCI]. Square shaped garage with no cove areas that would be obvious for a dedicated space.
Is it enough for the contractor to verbally tell the inspector that a piece of equipment is coming at the time of move in ?
Is it reasonable for the inspector to ask that the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
2) Empty garage with a duplex [in addition to a separate GFCI]. Square shaped garage with no cove areas that would be obvious for a dedicated space.
Is it enough for the contractor to verbally tell the inspector that 2 pieces of equipment are coming at the time of move in ?
Is it reasonable for the inspector to ask that the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
3) Empty garage with a duplex. The required GFCI is loaded off of a basement GFCI so that one duplex is protected, the other is not, but visually there is no difference between the two plugs.
Is it enough for the contractor to verbally tell the inspector that 2 pieces of equipment are coming at the time of move in ?
Is it reasonable for the inspector to ask that the nonGFCI receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
Would you have a problem with the inspector requiring the receptacle cover be labeled with the name of the equipment since the equipment isn't there ?
David