210.8(A)(2)

Ravenvalor

Senior Member
Would a finished wooden she shed with wooden floors about a foot above grade require all receptacles to be GFCI protected per article 210.8(A)(2)?

They don't plan to run any power tools. Just TV, minifridge, microwave, coffee pot, computer.

Thanks,
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Also, with the TV and other amenities present, sounds like this shed is not "limited to storage areas, work areas, and areas of similar use."

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The language of that section is poor....I have never seen a garage with the floor at grade level. They are always an inch or two above grade.

With this structure having the floor a foot above grade, the rule in 210.8(A)(2) does not apply.
 
Top