Okay, I see that now. I didn't go to the degree of viewing the schematic. Shame on me. :ashamed1:The title of the chart I linked to is "Autotransformer - 240 Primary Volts - 120/240 Secondary Volts - 1Ø". Their isolation transformers are on a different page, and they weigh about twice as much for a given kva:
https://www.hubbell-acmeelectric.com/p-133-240x480-120240
Cheers, Wayne
Well since Code requires a system that can be grounded such that it limits voltage to not more than 150 volts to ground [250.20(B)(1)], the only way these could be used compliantly is if the 240V source is ungrounded prior to grounding the center tap of one of these autotransformers... that's assuming it is used to derive 120V from 240V.Yep, the link you gave is definitely for autotransformers. If you dig further through their website you can find schematic showing that they have only one winding.
http://aspdotnetstorefront.hubbell-acmeelectric.com/Images/drawings/T253062.pdf
Also would like to know answer to this question.
I didn't read the instructions but wiring it to derive 240V from a 120V source shouldn't be a problem for compliance with the Code sections being discussed.