I have a question about the details of how the 125% factor for continuous loads is incorporated into the NEC. [This is my second attempt at asking, as I apparently buried the lead in my first attempt.]
215.2(A)(1)(a) calls for the conductors supplying a continuous load to have an ampacity increased beyond the actual load current by 25% of the continuous load current. [And 210.19(A)(1)(a) is similar.] The limitation is entirely due to the behavior of OCPD; since for continuous loads regular OCPD may trip at below the nameplate rating. So to avoid this nuisance (that could turn into a safety hazard if a user repeatedly resets a tripping breaker), the OCPD should be upsized by 25% of the continuous load current.
However, that is already covered in 215.3. And 240.4 already requires conductors to be protected in accordance with their ampacities, so when the OCPD is upsized, the conductors have to be upsized. That means the requirement of 215.2(A)(1)(a) is generally a logical consequence of 215.3 and 240.4, and at best redundant. But 215.2(A)(1)(a) also prevents the use of 240.4(B) [next size up rule] to comply with 215.3.
Real world example: an EVSE with a 48A output current (e.g. Tesla Wall Connector with the proper internal setting) is a continuous load, so the OCPD protecting it should be 60A. #6 NM cable has an ampacity of 55A because it is limited to the 60C rating. 240.4(B) allows protecting this with a 60A breaker [when 55A ampacity is otherwise sufficient per other sections of the NEC.]
So what is the hazard of supplying a 48A continuous load with cable with an ampacity of 55A that is judged sufficiently well protected by a 60A breaker when the load is non-continuous? Is this an intentional prohibition, or just a side effect of the redundancy of 215.2(A)(1)(a)?
Cheers, Wayne
215.2(A)(1)(a) calls for the conductors supplying a continuous load to have an ampacity increased beyond the actual load current by 25% of the continuous load current. [And 210.19(A)(1)(a) is similar.] The limitation is entirely due to the behavior of OCPD; since for continuous loads regular OCPD may trip at below the nameplate rating. So to avoid this nuisance (that could turn into a safety hazard if a user repeatedly resets a tripping breaker), the OCPD should be upsized by 25% of the continuous load current.
However, that is already covered in 215.3. And 240.4 already requires conductors to be protected in accordance with their ampacities, so when the OCPD is upsized, the conductors have to be upsized. That means the requirement of 215.2(A)(1)(a) is generally a logical consequence of 215.3 and 240.4, and at best redundant. But 215.2(A)(1)(a) also prevents the use of 240.4(B) [next size up rule] to comply with 215.3.
Real world example: an EVSE with a 48A output current (e.g. Tesla Wall Connector with the proper internal setting) is a continuous load, so the OCPD protecting it should be 60A. #6 NM cable has an ampacity of 55A because it is limited to the 60C rating. 240.4(B) allows protecting this with a 60A breaker [when 55A ampacity is otherwise sufficient per other sections of the NEC.]
So what is the hazard of supplying a 48A continuous load with cable with an ampacity of 55A that is judged sufficiently well protected by a 60A breaker when the load is non-continuous? Is this an intentional prohibition, or just a side effect of the redundancy of 215.2(A)(1)(a)?
Cheers, Wayne